View Full Version : Walk in cooler running 48degrees



cbslueck
14-04-2010, 05:55 PM
I am working on walk in cooler and it is running no colder than 48 degrees . The suction pressure is at 30psi and the hi side is at 210. I charged the unit propery and everything is working correctly. Anybody have any suggestions on how to get this thing below 40 degrees

Gary
14-04-2010, 06:05 PM
Obviously, everything is not working correctly... and pressures don't mean a thing if we don't know what refrigerant is in the system.

cbslueck
14-04-2010, 06:17 PM
R404A is in the system

Gary
14-04-2010, 06:35 PM
What does "charged the unit properly" mean?

DRAGA MICHAEL
14-04-2010, 07:57 PM
Hello comrad ,i had such senerio one time too,the reason is all about refrigeration load and refrigeration system capacity balancing.
for further clarity on how to go about,i shall request you to send dimensions of your walk in cooler and category, expected load,ambient conditions and final temperature you need to achieve.

simon@parker
14-04-2010, 07:58 PM
hello there not wishing to seem rude but have you got the pipes the correct way round ? not using the evap as the condenser an vice versa and did you install it and did you follow the instructions to the letter:confused::)

Brian_UK
14-04-2010, 08:54 PM
I would suggest getting a refrigeration engineer involved.

cadwaladr
14-04-2010, 09:05 PM
what is the air temperature going over the condensr[ambient] is the condensor clean.

Rigbee
15-04-2010, 10:09 AM
Start with the gas charge mate. Your pressures seem a bit low. How have you charged the system "properly"?

sork
15-04-2010, 06:24 PM
the timer stucks on defrost and the indoor fan is working, therefore mag valve is shut i. e constant back pressure.
switch off the unit , open controll box, turn on unit check for the s/c on timer.
good luck.

sork
15-04-2010, 06:33 PM
for charging gauge it up to high side,get your comparator check ambient temp add 15c on top, you must see exactly same psig as your calculation???????????
do you!

Magoo
16-04-2010, 05:00 AM
Hopefully you liquid charge system into the high side.
Vapour charging will give the exact problem you have described, on R404A.
magoo