We are using a Hitachi chiller unit (model: RCUP90AUZ).
Problem is, refrigerant pipe line is condensing & now in Bangladesh humidity level is around 65.
Can we insulating the pipe line like other chiller unit?
If the answer in not then why?

Sridhar1312
12-04-2010, 08:44 AM
Suction line from Evaporator to Compressor needs insualtion to prevent sweating of the refrigerant line. However the Liquid line need not be isulated as the temperature will be higher.

Sridhar1312
12-04-2010, 08:47 AM
The insulation thickness should be to prevent sweating of the lines.

Bashir01219
12-04-2010, 09:09 AM
my question is why the supplier or installer did not do that?
is it not reqired or he just missed it?

sedgy
12-04-2010, 02:53 PM
hi , if a pipe is cold you can insulate it ,if the pipe hot , you can not insulate it

CHIEF DELPAC
12-04-2010, 03:10 PM
Bash. Insulation of pipes was probably not in the contract. So none was applied. C.D.

ref717
12-04-2010, 06:53 PM
Bash maybe your supplier is not an HVAC contractor, they should have suggested and insisted that the suction line be insulated.

serviceman
12-04-2010, 09:38 PM
question that has condensed the pipe is the suction? INSULATING.

if the liquid line cycles fans

Bashir01219
13-04-2010, 03:26 AM
Thanks a lot to all of you, i think i got my answer

Bashir01219
16-04-2010, 04:40 AM
hi , if a pipe is cold you can insulate it ,if the pipe hot , you can not insulate it

Then what we have done with hot water, stem line, glass wool insulation?:)

little turtle
11-05-2010, 01:49 AM
We are using a Hitachi chiller unit (model: RCUP90AUZ).
Problem is, refrigerant pipe line is condensing & now in Bangladesh humidity level is around 65.
Can we insulating the pipe line like other chiller unit?
If the answer in not then why?
It seems funny if suction line is not insulated
:)

Bashir01219
11-05-2010, 03:56 AM
It seems funny if suction line is not insulated
:)
yes it is.......