mianrizwan
04-04-2010, 09:07 AM
i have three phase compressor(r 502) its take 3.5 ampire. there is no compny data on this compressor. now the problem is that how can i find the hp or tonage of the said compressor.

goshen
04-04-2010, 01:03 PM
Hi i would say only a calculated guess !!!but u must give more data ,voltage,piping diameter???
u might look at the txv if fitted !!

mianrizwan
05-04-2010, 04:56 AM
voltage=380, Discharge = 1/2, suction line = 5/8 inch and with txv.

nike123
05-04-2010, 09:34 AM
Check if there is any number/letter pressed in metal housing of compressor and post here if you find anything.
Photo of compressor could help.
Also, give us all data written on TXV.
Also, give us all data of unit where that compressor is located.

mianrizwan
05-04-2010, 04:06 PM
there is no name plat or other printed metarial on the compressor. there is no data on the TXV. and the compressor is 3 phase. and it ampere are 3.5.
there is no data on the compressor txv or other place of the system.

goshen
06-04-2010, 05:16 PM
Hi aprox 2 hp motor if running at nominal current.

ref717
06-04-2010, 06:01 PM
Your new 3-phase motor HP rating is 2.5 HP.

mianrizwan
08-04-2010, 10:38 AM
but how u can say that this is 2.5hp plz give other information or deta.

goshen
08-04-2010, 10:52 AM
but how u can say that this is 2.5hp plz give other information or deta.
Hi this is data based on motor current tables
for 380-400 volts :)

ref717
08-04-2010, 03:22 PM
but how u can say that this is 2.5hp plz give other information or deta.


i assumed you have a new energy effecient motor.
i used theoretical computation to get he rated motor HP as follows :

HP = Rated Ampere x Voltage x power factor x cube root of 3 (3-phase motor) then divide by 746 (to get HP unit).

ref717
08-04-2010, 03:31 PM
correction guys, it is square root of 3 and not cube root,sorry for the typo error.

goshen
08-04-2010, 05:07 PM
i assumed you have a new energy effecient motor.
i used theoretical computation to get he rated motor HP as follows :

HP = Rated Ampere x Voltage x power factor x cube root of 3 (3-phase motor) then divide by 746 (to get HP unit).
Hi yes u can calculate ,but for fast referal u can use a table like this example
http://www.lostock-electrical.co.uk/html/motor_rating.html
:)

ref717
08-04-2010, 05:11 PM
thanks for the data table my friend,its also a good reference...

mianrizwan
09-04-2010, 11:23 AM
there is no deta on the compressor i have told you.

goshen
09-04-2010, 01:22 PM
there is no deta on the compressor i have told you.
Hi dear sir:
u gave us no data! only current, so based on that data we use it to corallate it with the closest,compatible unit!!!;)