View Full Version : CityMulti on BACnet
I do have 3 black BACnet boxes on CityMulti. No G50 or GA150. Everything on X-cite IQ3; 963 supervisor. So, I can't get fault codes.
Question: how to collect fault codes from Mitsu BACnet controller on Air Con side?
Any free software, or for reasonable price?
/I can't open outdoors, and here ne PAR-21/.
Thank You
P.S.: :rolleyes: I haven't design system, client cut on GA150
laf100
05-04-2010, 09:17 PM
As far as I know, fault codes are not "passed on" through the a BACnet gateway, can you nott connect a par27 or Monitor Tool PC somewhere on the system? If you cannot "open outdoors" how will you repair the fault if it is an outdoor unit problem?
I do have 3 black BACnet boxes on CityMulti. No G50 or GA150. Everything on X-cite IQ3; 963 supervisor. So, I can't get fault codes.
Question: how to collect fault codes from Mitsu BACnet controller on Air Con side?
Any free software, or for reasonable price?
/I can't open outdoors, and here ne PAR-21/.
Thank You
P.S.: :rolleyes: I haven't design system, client cut on GA150
you can get the fault codes from the LCD display on the outdoor unit if the Bacnet device is a BACHD150 you can connect a m-net tool to it. Or get the trend contrioller set up to bring the faults thru the controller will be able to do this.