View Full Version : TG-V1 Guarded access
Oldmanfrigy
15-03-2010, 06:55 AM
Could ayone tell me how to get into guarded access to clear code 71 on a TG-VI controler.
I can get into uP-V1 and SR2 for code 71 and 128.
There is not enough buttons.
Thanks for all the help that keeps coming as we pool our knowledge.
:cool:
DaButcher
15-03-2010, 11:48 AM
Entering Guarded Access Mode
Guarded Access Mode is entered by pressing
the “Select” key until [ddr] appears on the
display. Then press and hold the “T/K” key for
5 seconds. The [H4t] screen will appear. The
[H4t] screen is the first screen in the Guarded
Access menu. If no other key is pressed for 30
seconds while in Guarded Access mode the
microprocessor will exit Guarded Access mode
and the display will return to the Standard
Display.
Oldmanfrigy
16-03-2010, 10:48 AM
Thanks for your help again.
carrier_trained
24-03-2010, 07:13 AM
You should have 5 buttons, "select,up,down,enter, and TK"
Make sure cycle-sentry is off,press "select" till you get to "ddr 45", then hold down the "TK" button for 6seconds, you be in guarded access, scroll through till the alarm is displayed, then press enter to clear.
Let me know how you go.
cheers. ;)