PDA

View Full Version : trane chiller; starter did not transition



oupak
14-03-2010, 09:43 AM
CAN SOMEONE PLS HELP: THE TRANE CENTRIFUGAL CHILLER IS ALWAYS SHOWING THE FOLLOWING ALARM; STARTER DID NOT TRANSITION...the motor starter is a Y delta with transition resistors...

ragards

Lowrider
14-03-2010, 10:03 AM
On all the relais there is a contacter. If one off those is at fault the controller will give the transition fault. If the chiller is set up as part winding instead of Y-delta the same error will come.

moideen
15-03-2010, 06:13 AM
CAN SOMEONE PLS HELP: THE TRANE CENTRIFUGAL CHILLER IS ALWAYS SHOWING THE FOLLOWING ALARM; STARTER DID NOT TRANSITION...the motor starter is a Y delta with transition resistors...

ragards

i thing this is due to control fault.check compressor contactor and its auxilaries.

Moideen-dubai

goshen
15-03-2010, 07:21 PM
CAN SOMEONE PLS HELP: THE TRANE CENTRIFUGAL CHILLER IS ALWAYS SHOWING THE FOLLOWING ALARM; STARTER DID NOT TRANSITION...the motor starter is a Y delta with transition resistors...

ragards
Hi does the chiller go through a contactor check 5 secondes before starting ??
if it does u have a problem with your auxilary contact that tells the chiller it ended transition .
if it dosent run the test check your wiring or a burnt coil .
u could run a test on the staret using the tsest function ,beware to drop the maines before running the test .:)