12-03-2010, 08:05 AM
3420Hi

can anyone confirm to me what the arrow means on the srtainer.

nike123
12-03-2010, 08:27 AM
Corect direction of flow!

casino
12-03-2010, 08:37 AM
cheers nike123 as this is what i thought, so next question is, is the strainer round the wrong way bearing in mind that it is on the liquid line as to me its round the wrong way??

nike123
12-03-2010, 08:46 AM
That line is bidirectional since this is heat pump!
In heating mode it is correctly oriented and protect capillary and 4 Way valve from clogging.
Sometimes it is another strainer on bigger diameter line coming from indoor unit or somewhere else in circuit with same task of protecting capillary tube and 4-way valve . In indoor unit it does not have to protect anything from clogging, therefore it could be oriented like that.

casino
12-03-2010, 08:55 AM
sorry this is my fault, i should of mentioned that this unit is cooling only.

nike123
12-03-2010, 09:01 AM
sorry this is my fault, i should of mentioned that this unit is cooling only.

Do you have refrigerant diagram of unit or make and model#?

casino
12-03-2010, 09:05 AM
Yes, see attached. Not the best drawing in the world.3421

it is the 71 model.

nike123
12-03-2010, 10:32 AM
Yes, see attached. Not the best drawing in the world.3421

it is the 71 model.
That is not refrigerant diagram, that is exploded view!

casino
12-03-2010, 03:11 PM
i have no refrigerant diagram.

old gas bottle
12-03-2010, 03:35 PM
looks like a discharge muffler to me, acts a bit like your car exaust if you like,the arrow means the canteen is a thater way :D just the direction of flow for the guy who,s fitting it as its looks the same from both ends.;)

nike123
12-03-2010, 06:56 PM
Make and model# please!

casino
31-10-2010, 09:50 PM
Apologies for not coming back to this.

Just to resurrect this and finalise. I received a new strainer and the arrow was pointing the same way, how odd, to me anyway.
As this was a new one I did not question it.
This unit also had an indoor coil that was leaking. Replaced and working ok.

Still find it odd the arrow pointing in the opposite direction of flow..

C.

Brian_UK
31-10-2010, 10:37 PM
Maybe it means this way up.

Anyway, thanks for updating this thread.

NoNickName
01-11-2010, 10:37 AM
It's strange that the liquid line comes from the middle of a condensing coil. I see why nike123 thought it was a heat pump.