PDA

View Full Version : Daikin outdoor unit MY90CJY1



Rmon
07-03-2010, 02:55 PM
Hello.
I´m having some problems with a DAIKIN outdoor unit MY90CJY1 .:confused:
It´s a unit 5 to 1 ,concealed indoor units non inverter -R22.
Anyone have the service manual for this unit?
Thanks

VRVIII
07-03-2010, 08:18 PM
Hi Rmon,

You should be able to download the manual from Daikin web site (extranet) if you register.

What's the problem with the unit? What info do you require?

Rmon
08-03-2010, 10:54 PM
Hi
I´m searching for the service manual.
Where is it possible to download it?
There is no possibility to work in extranet In daikin site of Portugal .
I´m running the machine in heat pump.
In line of service i have an evaporation of +5ºc, in the line of gas or liquid the pressure is very low ,above 7 bar ,and the discharge temperature is low.
It seems to be something wrong with the mechanical part, because the compressor works.
Some one tell me that it could be the EEv .
The Daikin service Tells me that this is a very complex machine .
Can you help?
Thanks