PDA

View Full Version : ICAD 900 problems



tyrrell6w
07-03-2010, 07:10 AM
good day to you all

where having some problems using a icad 900 with a icm65
\we use it for defrosting our plate freezers on board an dutch frezing trawler
now the problem we are have is
it seem the valve is not opening quickly
when we give the valve some pre opening its going oke for several times
then over a period of time (approx 1 hour)
The pre opening is disserpearing
and the valve or icad seem to be to late to open again

we trided re callibrating
checked all the setting
everyting seem to be in order
after recalibration the vale works fine by th way
but after approx 1 hour the malfuntion begins again

the valve is in a co2 system

hope somone can help me

berst regards jack eelman

cricri
10-04-2010, 08:11 PM
Your problem is that some moisture, when it's frosted, is locking the actuator to rotor sleeve. you should remove the actuator, warm and dry the sleeve and apply greeze with a deep freezing point. it will prevent moisture to get in.

RANGER1
11-04-2010, 01:29 AM
Danfoss recommend gland heater be installed on ICAD for any application minus 30 C & lower .

Grizzly
11-04-2010, 09:04 AM
Cricri has pin pointed the logical cause and Ranger's advice is spot on!
We even fit them on chill applications.
Well worth acting upon both recommendations.
Grizzly.

cricri
12-04-2010, 09:10 AM
Hello,

I'am back to my office, you 'll find some quote of an instruction delivered with a new ICAD900