View Full Version : return air , please help me,!!!



vietvho
01-03-2010, 01:21 AM
Hi, friends !!!
i have an room which just need 18000 btu/h !!!
But i use 21000 btu/h .
Now i have problem , the temp is alway lower than the set temp !!! (ex: i set temp at 23 the room temp will be 21 ) so,can i fix this problem ???
Thank , a lot my friends !!!
Thank forum and best development !!!

stefs_cruiser
01-03-2010, 01:36 AM
Set 25 ;-)

If it is an inverter then most units will go to lowest running power, for one degree past set point, before switching off. Best option is to set a slightly higher temp.

mad fridgie
01-03-2010, 01:37 AM
Hi your rating of your AC is just a number at one point, you may be getting more or less depending on many factors.
I would say just turn up thermostat by 2C (it may just be a calibration issue) When testing control temps you must have thermometer in the same place as AC thermostat sensor.
If AC is way to big, you tend to find the the room will have very high RH.

Gary
01-03-2010, 01:48 AM
Also, set the fan to its lowest speed.

vietvho
02-03-2010, 12:52 AM
thank friend !!!
the sensor of remote and return air is the same at the temp set in remote . but the temp of room is lower than 1.5 to 2 deg !!!
Thank friends
thank forum and best regard !!!

Brian_UK
02-03-2010, 07:47 PM
If the return air is warmer than the room it is because the return has picked up the load from the room.

More details as to the type, location and airflow around, from and back to the unit would be useful.

vietvho
10-03-2010, 07:26 AM
Hi, friends !!!
After have a full tracking with my VRV3 system i have some parameter :
-The set temp = 23 deg (the temp want to set for the room)
- the return air temp = 23 deg
- the remote sensor temp = 23 deg
- The temp of room = 21.5 deg ????
What were happen ?
our group had tried our best to fix this problem ....
ex :- setting to use only remote sensor
-change remote position
-check all the sensor
but it seem not have any effective .
Could you hep me , my friends?
Thank you a lot .
Thank our forum .
Best Kind !!!

Brian_UK
10-03-2010, 06:48 PM
Whereabouts is the remote controller in relation to where you are measuring the room temperature?

What happens to the room temperature when to increase the control temperature by 2 degrees?

vietvho
11-03-2010, 02:07 AM
hi, friend !!!
Have a nice day (^_^)
thank you for your advice
when i set the time of room = 24 deg
The remote sensor temp = 24
the return air sensor = 24
And the temp of room is maintain at 22-22.5
Thank you a lot !!!
thank forum
Best kind and best regard

vietvho
13-03-2010, 12:51 AM
:rolleyes: oh, friends !!!
Why you do not help me ?
I am tire so much for that problem
who can give me an advice ???
Thank you alot
thank forum !!!
Best regard !!!

Toosh
13-03-2010, 01:06 AM
:rolleyes: oh, friends !!!
Why you do not help me ?
I am tire so much for that problem
who can give me an advice ???
Thank you alot
thank forum !!!
Best regard !!!


Your main problem is that the A/Cis to big for the area being conditioned keep setting the temp higher till you are happy

Toosh

Sridhar1312
13-03-2010, 03:34 PM
The unit is over sized. Not only temperature will go down humidity also will increase. Best thing is to change the air quantity to suit your requirement then the thermostat can take over to modulate within a range.

nike123
13-03-2010, 04:17 PM
With what instrument you are measuring that temperatures? Is it calibrated?
Or you are giving us temperatures of unit thermistors read from remote control and actual room temperature read from some measuring instrument.

It looks to me that your measuring instrument is off by 1.5°C

back2space
15-03-2010, 12:26 AM
Turn the fan speed down to the LOWEST you can select. This will mean less air circulation so less output from the unit.

particulary useful if the unit is oversized.