27-02-2010, 04:13 PM
hi ,

The picture i included is one of a heat exchanger,the tube is the exit liquid pipe
from a freezing application (hope this is the right place to post this)
It struggled for a long time with low pressure issues.
i think this fault is due to bad brasing (20%)
instead of 80 %

have you guys ever seen this kinda thing before ??
and what do you think :cool:

thank you

monkey spanners
27-02-2010, 05:24 PM
Looks like there is something blocking the pipe??

Iceman 386
28-02-2010, 01:07 AM
looks like you could of had a liquid slug shot through the system for some reason
need more info about the system

frederik79
28-02-2010, 09:49 AM
monkey spanners
my theory is liquid got under the copper...(look at the first pic)
pushed the copper blocking the pipe.
can't get any other good reason why this happened.

monkey spanners
28-02-2010, 12:55 PM
I've seen something similar in a vibration eliminator, used to cause hp trips on start up but once system was running it worked ok.