View Full Version : Fault 052 and 055 Carrier 30GTN100--C620



WallyHoneywell
26-02-2010, 10:58 PM
Hello,
Carrier 30GTN100--C620 with ComfortLink Reciprocating Liquid Chillers keep having fault T052 (Circuit A, Compressor 2 Failure) and T055 (Circuit B, Compressor 1 Failure) we had the service teach from factory came and could not find any thing wrong, and the fault came couple of times in a day, vendor suggested to upgrade firmware to increase percentage voltage imbalance.
Thanks
Wally

moideen
27-02-2010, 05:29 AM
Hello,
Carrier 30GTN100--C620 with ComfortLink Reciprocating Liquid Chillers keep having fault T052 (Circuit A, Compressor 2 Failure) and T055 (Circuit B, Compressor 1 Failure) we had the service teach from factory came and could not find any thing wrong, and the fault came couple of times in a day, vendor suggested to upgrade firmware to increase percentage voltage imbalance.
Thanks
Wally
hi wally,this alarm will occur due to the high discharge pressure,loss of charge and fault cpcs board.note the DP at peak time. Being affect the both circuit,i think due to the high discharge pressure.

Moideen-dubai:off topic: