View Full Version : Condensate lift pump



coolhandlew
23-02-2010, 05:51 PM
I was doing some servicing today on splits, chlorinating drain pans and bucket pumps etc. Wouldn't it be good if you could test a unit's lift pump from a setting on the remote controller.

Maybe you can and I don't know about it, if anyone does I'd be grateful to learn. (Daikin/Mitsi eg.)

Brian_UK
23-02-2010, 07:19 PM
Come on now, that would make life just too easy. :D

VRVIII
23-02-2010, 07:49 PM
Come on now, that would make life just too easy. :D
Daikin easy life it is then :D:D:D

Option 1 (all daikin indoors with internal pump)
Switch the unit on in cooling mode and the pump will operate when indoor is thermo on, the float switch is only used as a sefety device.

Option 2 (vrv indoors with internal pump)
Switch off controller
Select fan only
press test button until test is displayed on controller display (3 or 4 times)
Switch on controller and pump will operate

Andy AC
23-02-2010, 09:24 PM
On the modern mitsi heavy units (R410a) you can run the pump from the test button menu on the controller (wired)

Andy

Brian_UK
23-02-2010, 11:01 PM
VRV, thanks, yes option 1 has always been, I'd forgotten.
Option 2, good to know.

Andy, also good info.

Thanks.