View Full Version : Oil volume in custom refrig circuit



alexilla
22-02-2010, 06:41 AM
Hello. I am new to the refrigeration industry. On a custom built refrigeration circuit, are there any tools or formulas to use in calculating the proper volume of compressor oil to use? Or is there a rule of thumb? Any help would be greatly appreciated!

gregd1401
22-02-2010, 12:00 PM
alexilla
The oil is for the compressor, not for the refrigeration circuit or any other component. Correct pipe sizing is the primary concern with any refrigeration system to ensure proper oil return.

alexilla
23-02-2010, 05:26 AM
So, what your saying is that the volume of compressor oil contained within a refrigeration circuit is strictly proportional to the size/type of compressor(s) used?

gregd1401
23-02-2010, 09:29 AM
Exactly right. If the system piping is correct oil return will not be a problem. However there are exceptions to the rule as in flooded and ammonia systems. Also you should never add oil to a system unless you know where the existing oil has gone.

alexilla
24-02-2010, 04:41 AM
Thats exactly what I wanted to know. Thank you for your help

gregd1401
24-02-2010, 05:09 AM
Glad to be of assistance.