PDA

View Full Version : Carrier 30GH245



yanev22
08-02-2010, 08:59 AM
Hello !

I write for first time in this forum .

I have wonder if someone can tell me the answer.

I have a Carrier Air cooled chiller , Model 30GH245
800 KW cooling power , with 8 reciprocating semi-hermetic compressors 06E. 2 circuits and Refrigerant R22.

Can this chiller be using for ice rink somehow ?
The ice rink need about -4 , -5 degrees .

Thanks in advance !

nike123
08-02-2010, 09:21 AM
I generally don't see reason why not for any chiller if you use glycol solution and you are within operating envelope of compressor.
http://www.carlylecompressor.com/Files/Carlyle_Compressor/Local/US-en/pdf_files/06E_OperatingEnvelope.pdf

Brian_UK
08-02-2010, 07:24 PM
Documentation if you need it...
http://eto.carrier.com/lit.asp

moideen
09-02-2010, 04:27 AM
[quote=yanev22;177141

Can this chiller be using for ice rink somehow ?
The ice rink need about -4 , -5 degrees .
/quote]

For ice rink application glycol leaving temperature must be -8C during freezing. And -4, -5C to hold about 15mm thickness of ice. So you should expect the evap. pressure is from 2 to 2.3 bar and check LP protection of the chiller.

30 GH chiller can’t use for low temperature. This has designed for comfort cooling. It has programmed setting in accordance the medium temp. Applications. Especially 06E compressor for only medium or high temperature applications.06CC compressor using for low temp.