hi all
on a cellar cooling system what would give you low suction and discharge temps.
thanks

taz24
04-02-2010, 12:14 AM
hi all
on a cellar cooling system what would give you low suction and discharge temps.
thanks


In This weather??

The tempreature!! When its cold the suction and head pressure will be low.

A blocked evap or faulty evap fan.

System short of gas.

A damaged or faulty TEV.

Theres a few things to be going on with.

taz.

.

sean1
04-02-2010, 12:22 AM
hi taz
thanks for the reply
i understand the low temp but at what point would you call it that? or how would you check for it?
i had a cellar cooler today at 1 barg low side and 8 barg high with a ambient of 5 celcius with a clear glass.
it running on r407c

taz24
04-02-2010, 12:27 AM
hi taz
thanks for the reply
i understand the low temp but at what point would you call it that? or how would you check for it?
i had a cellar cooler today at 1 barg low side and 8 barg high with a ambient of 5 celcius with a clear glass.
it running on r407c


I have responded to your other post.

taz

.

sean1
04-02-2010, 12:47 AM
thanks taz apreciated

mcunliffe4
13-02-2010, 12:49 AM
sounds like tev faulty or restriction in liquid line