View Full Version : Toshiba MAR-F102 HTM8-PE VRV Issues...



terminator
25-01-2010, 06:50 PM
Hi Guys,

Wonder if you can help.

We had very little time on site today, but here's what we found.

System not running, switched off and then on. Made noises like it was going to run, condenser fan started then stopped. Nothing further, no compressors running etc.

It serves 8 large rooms, but could only get into two, and took the following fault codes..

03 07 01.1d
041c 01.1d

There are 3 boards in the unit....

Interface (nothing on the led displays - all dead)

mcc 1251 - the inverter control board

mcc 1252-04?

The two smaller boards are connected with a ribbon cable. If you disconnect this and restart, the fixed speed comp will run for 5 mins, off for 5, on for 5 etc...

When you reconnect the boards, the unit will not run.

Any ideas would be great. Never worked on a Toshiba vrf before.

G.....:D

slaphead
26-01-2010, 08:57 PM
Your fault is the 1d code, locked rota / high current.
Generally linked to mechanically locked compressor

sinx712
03-02-2010, 05:41 PM
HALLO,
if you have any general electric cut in your installation you must initialised your electronic regulator of liquid R22?
you have tow broch for doing this operation at your indor distridution of a gaz you must inter a code for this ...

sinx712
03-02-2010, 05:48 PM
Service Manual
Air Conditioner - Multi Split Type System
sinx712@hotmail.fr
i can give you this docs