PDA

View Full Version : 30gx probleme



farhang
23-01-2010, 09:18 AM
I am facing problem with Carrier chiller model 30gx227a0224nee . I've just change the CPM board of compressor A2. although the LED red flashlight turn on, the green one dosn't work and the compressor A2 dosn't run. It would be helpful if you send me the address of DIP swich on the CPM board and tell me why LED green flashlight dosn't work.

Thanks a lot
Farhang

Brian_UK
23-01-2010, 04:39 PM
Is the board set for the correct compressor?

Green LED shows a communication error, check fault codes.

Do you have a manual for the unit?

If not try here--
http://eto.carrier.com/lit.asp

Gibbo
23-01-2010, 06:43 PM
Check dip switch settings on old CPM board then set new CPM the same. Then CPM will communicate

farhang
24-01-2010, 08:03 AM
Dear Gibbo

I checked every thing and they all seem alright. communication between A2 and B1 is ok, A2 and A1 is ok, but again there is a problem in green flash and it dosen't work. I don't know what address should I give to the board? there are 8 dip swith and 4 more dip switch. could you please help me?

thanks in advance for your kind attention.

Gibbo
24-01-2010, 09:41 AM
match your dip switch settings from the old board to the new board.

farhang
25-01-2010, 05:29 AM
match your dip switch settings from the old board to the new board.
Hi

I have the slave boards address in manual but the address dosen't match and I want the address that match the board and let it to run.