humphreymech
18-01-2010, 11:21 PM
We have new supermarket with Novar controls. I have not worked on racks with this control only HVAC equipment, The Rack's I have worked on have CPC or E1,E2 and this control doesn't have schematic you can read. Called tech line because all compressor were on and was having problems with oil reset. Tech line told me the Compressor Board was bad? This compressor board has 24v in and then switching relays with duty of 250v and small toggles that have auto on and off with led for each relay. Tech line says should have 9 volts at bottom switch relay but have line volts to ground? I found a bypass switch in bypass. Restore to normal position and system is ok. It look to me like should be line volts at relay and teck line full of it. Please let me know what you think or if you have a novar schematic.