View Full Version : high temperature of the discharge



ahmed_helmy226
13-01-2010, 12:37 PM
Hello
Has a problem with the refrigeration compressor screw, after you Increasing compressor oil and when you start to note the high temperature of the discharge I have to make sure that the valve fully open suction as well as ascertain the level of oil in the oil separator is controlled with the knowledge that the oil temperature is not high, as well as pressure Expulsion is not high
Please advise and Thank you

andy c
14-01-2010, 10:54 PM
It sounds like the screw compressor is running at low capacity. Check that the loading up valve is operating correctly.