Hi Chaps
wondered if anyone could help me.
I have a problem with a Daikin vrv system which has 21 indoor units each with BSQV boxes.
At present we have only been to site for a quick look and they have reported 1 unit not heating,the unit is furthest away from the condenser,the only unit on the ground floor.
when we attended site during the day most the other units were in heating mode and although it was only a quick visit they seemed ok (no report otherwise)
the unit in question was running but not heating.
I attended site the next morning and the unit was running fine in heating mode but after a while it stopped heating, this problem apparently happens all the time, heating one minute and then not the next.
I have 2 ideas, either low gas charge, maybe when there is more demand from other fan coils this unit is starved of refrigerant or faulty solenoid/bsvq box.
I am due to re visit site shortly to thoroughly check the system,
Obviously i want to try to avoid reclaiming and recharging the system.
Does anyone know how to carry out a test on the BSVQ box or any other advice
thanks
wondered if anyone could help me.
I have a problem with a Daikin vrv system which has 21 indoor units each with BSQV boxes.
At present we have only been to site for a quick look and they have reported 1 unit not heating,the unit is furthest away from the condenser,the only unit on the ground floor.
when we attended site during the day most the other units were in heating mode and although it was only a quick visit they seemed ok (no report otherwise)
the unit in question was running but not heating.
I attended site the next morning and the unit was running fine in heating mode but after a while it stopped heating, this problem apparently happens all the time, heating one minute and then not the next.
I have 2 ideas, either low gas charge, maybe when there is more demand from other fan coils this unit is starved of refrigerant or faulty solenoid/bsvq box.
I am due to re visit site shortly to thoroughly check the system,
Obviously i want to try to avoid reclaiming and recharging the system.
Does anyone know how to carry out a test on the BSVQ box or any other advice
thanks