PDA

View Full Version : York YDAJ gsi reciprocating chillers



vinod
08-01-2010, 06:48 AM
York YDAJ gsi chiller display system hanged. no any button functioning, and cannot getting any information.(chiller is working properly)
Display board replaced and checked, but the situation is still the same. Pl give a solution.

moideen
08-01-2010, 02:56 PM
York YDAJ gsi chiller display system hanged. no any button functioning, and cannot getting any information.(chiller is working properly)
Display board replaced and checked, but the situation is still the same. Pl give a solution.

check ribbon cable which connecting display board to processor board.replace that.

expecting your response

Moideen-dubai

vinod
09-01-2010, 03:10 AM
Ribbon and display board replaced. but still the same situation

moideen
09-01-2010, 04:33 AM
it might be the trouble of Power supply board.check the voltage from power supply board J3 terminal,it should be 12VDC healthy.and also check the J1,J6 terminal from processor board,wire loose or misplaced.

Moideen-Dubai:off topic:

al
09-01-2010, 05:47 PM
i think there should also be a 5vdc test point on the board, check this also. This problem can(although rare) be caused by a faulty transducer or sensor.

al

Grizzly
09-01-2010, 07:20 PM
To add to the above excellent advise!
Check if the control panel emergency stop device. Or any remote emergency stop devices are off?

vinod
10-01-2010, 07:08 AM
The problem solved by replace the key pad. Thanks to all.