PDA

View Full Version : FXDQ static pressure adjustment



multisync
05-01-2010, 08:06 PM
Reading the manual it states:




The air flow is set to “standard” before leaving the factory.
It is possible to switch between “standard ESP” and “high ESP” via
the remote control.



But it doesn't state how!


Multi

VRVIII
05-01-2010, 08:27 PM
Reading the manual it states:







But it doesn't state how!


Multi


[/size][/font]

Hi Multi,

This is ususlly done by changing field setting 13-5-01 to 13-5-02 for high static, however you would need to confirm the full model number to verify this is applicable to your unit.

FXDQ????M/NA/P :)

multisync
05-01-2010, 08:50 PM
Hi Multi,

This is ususlly done by changing field setting 13-5-01 to 13-5-02 for high static, however you would need to confirm the full model number to verify this is applicable to your unit.

FXDQ????M/NA/P :)


Full model number : FXDQ32 PVE simplifed remove btw

Thanks :D

VRVIII
05-01-2010, 09:14 PM
Full model number : FXDQ32 PVE simplifed remove btw

Thanks :D

Hi,

Yeah 13-5-02 is the correct setting :D:D:D

P.S. you've got mail ;)