PDA

View Full Version : Open Type Compressors



shogun7
07-01-2005, 05:38 AM
Refrigerant and oil leakage is a factor on open drive centrifugal chillers. As the drive shaft from the
compressor drive unit is connected to the open motor outside of the compressor housing a “rear seal” must
be used to ensure minimum leakage of oil and refrigerant through this seal. Open drive seals are designed
to minimize leaks in two modes during operation of the chiller when the compressor shaft is rotating and
during a shutdown period when the shaft is stationary. As seals are designed to
accommodate both conditions, along with normal contact wear on the seal, both oil and
refrigerant will leak through the seal. Refrigerant loss increases as the seals dry, during long
shut down periods. The industry average loss of refrigerant entrapped in the oil leaking through
the rear seal is 2% of the full chiller refrigerant charge annually. Oil leakage varies and is
measured by collection in measured containers
My question is ..are these OK to use in EU? :confused:

Brian_UK
07-01-2005, 10:15 AM
I should imagine that hermetic as against open-drive would be the preferred option nowadays. Mind you I don't deal with these beasties so hopefully someone more qualified should have the answer.