02-01-2010, 04:43 AM
i have a reach in freezer that is not getting to temp im trying for 0 deegres F using 409a retrofitting r12 i ave 1 psig suction and 150 psig head pressure airflow is good through the coil but i can only get it down to 15 degrees and then the suction line starts creeping with ice after a hitting 15 im out of ideas as of right now

monkey spanners
02-01-2010, 12:46 PM
Is it just after replacing the R12 with R409A that the problem started?

If its a capiliary system you will need less R409A than R12 because R409A weighs less for the same volume. So it could be overcharged.

Kp3
02-01-2010, 01:11 PM
ur saying that freezer on r12 are u sure its wasnt r502 = r408a

Jesus Quijano
02-01-2010, 11:43 PM
the system already had 409 in it and it is direct expansion wat i did to it first was recover nitrogen vaccum because the pressures were 350 hi and 15 low and the liquid was not even hot to the touch to be doing 350psig which should be more then 150 degrees F but when i recharged it to where its at now (which means there was a lot of noncondensables in the line) and at 1 psig it should drop the temp to at least 8 degrees..... anything im over looking? somethng weird about 409 i should know???

nike123
03-01-2010, 08:07 AM
http://www.sdm.kiev.ua/eng/refregerants/service3.html

monkey spanners
03-01-2010, 02:31 PM
Is this a capiliary or TXV system?

I'm wondering if it has a restricted capiliary and a previous tech had overcharged it to bring up the suction pressure.

Jesus Quijano
03-01-2010, 03:49 PM
thats was what i thought when i cleaned it out but when i charged it the capilary was clear i tripled checked it and it flows perfectly and now the pressures stay steady but temp will not drop... im starting to think this was a cooler and the condensing unit doesnt have the capacity to bring it down to 0 could that be?

big h cooling
03-01-2010, 03:52 PM
sounds like you have a restriction in the pipe work

Jesus Quijano
03-01-2010, 07:53 PM
thank you all for your replies but i learned something new today............. do not ever trust extech multimeters temperature sensor they work perfect all the way down to 40 degrees F but any lower and it gives you a reading way off

Kp3
03-01-2010, 07:56 PM
ive only seen r12 as a freezer a on chest freezer. i would suggest getting cond unit details and check with ur local wholesaler that unit has the duty to pull it down to -21degrees