26-12-2009, 03:24 AM
Hi,
I have query about a roof top APAC reverse cycle air conditioner serving busy grocery shop. we have set it to run on heating as the shop gets too cold with the refrigerated display counters.
Temp set to 22 degrees, shop temp is close to 19 degrees. Ambient temp is 28-32 degrees weekly averages.
HP switch is factory set to cut out at 360 psi.
It trips out on high pressure now and again
Its a R22 unit and running pressures are within limit i.e 68 lp,240 hp PSI.
All filters are clean, indoor and outdoor fans are running and, running currents are within nameplate ratings.
Air flows are good with no restrictions in duct work.
The fresh air intake is fully closed via servo controlled dampers and the unit works on an economy cycle system whereby if outdoor temp exceeds 32 degrees, outside air dampers open and the compressor and out door fan go off and now the indoor fan recirculates the outside air.
I had feeling that during defrost (de-ice) cycle, the pressure might be rising above the 360 psi cut out which is factory set and tripping it. probably the de-ice control sensors or the de-ice time out circuit may need checking???
any advice on how i can test the de ice cycle, i thought of inserting the sensors in a frozen ice pack to emulate the cycle??
Of course it has to be monitored to confirm my doubt.
Any assistance will be highly appreciated guys.And a MERRY CHRISTMAS
cheers
I have query about a roof top APAC reverse cycle air conditioner serving busy grocery shop. we have set it to run on heating as the shop gets too cold with the refrigerated display counters.
Temp set to 22 degrees, shop temp is close to 19 degrees. Ambient temp is 28-32 degrees weekly averages.
HP switch is factory set to cut out at 360 psi.
It trips out on high pressure now and again
Its a R22 unit and running pressures are within limit i.e 68 lp,240 hp PSI.
All filters are clean, indoor and outdoor fans are running and, running currents are within nameplate ratings.
Air flows are good with no restrictions in duct work.
The fresh air intake is fully closed via servo controlled dampers and the unit works on an economy cycle system whereby if outdoor temp exceeds 32 degrees, outside air dampers open and the compressor and out door fan go off and now the indoor fan recirculates the outside air.
I had feeling that during defrost (de-ice) cycle, the pressure might be rising above the 360 psi cut out which is factory set and tripping it. probably the de-ice control sensors or the de-ice time out circuit may need checking???
any advice on how i can test the de ice cycle, i thought of inserting the sensors in a frozen ice pack to emulate the cycle??
Of course it has to be monitored to confirm my doubt.
Any assistance will be highly appreciated guys.And a MERRY CHRISTMAS