View Full Version : The condenser is 15 metres below the compressor?



ArtMal2009
16-12-2009, 04:37 PM
Will I find technical documentations about making the cooling installation where, where the condenser is 15 metres below the compressor?
How to make the return of oil on the liquid?
What are there problems with the return of oil?

Brian_UK
16-12-2009, 07:23 PM
Whereabouts is the evaporator?

ArtMal2009
17-12-2009, 09:33 AM
The evaporator is 1 the metre over the compressor - precise air conditioner.

Gary
17-12-2009, 05:17 PM
Oil won't be a problem as the liquid will carry it easily.

The problem would be needing to raise the high side pressure in order to lift the liquid back up to the evaporator.

This would be a good system to add a liquid pump.