View Full Version : HP & LP Switches



Deano240
14-12-2009, 07:52 PM
Hey can any one explain how to set up LP and HP Switches please ? any info would be of great help ! thanks

Brian_UK
14-12-2009, 07:56 PM
The HP switch should be set to below the pressure relief valve if fitted.

It should be set according to the manufacturers design requirements also.

On a more basic level, the instructions that come with the switch will give the mechanical aspect of the switch itself.

What function are you wanting the LP switch to do?

Deano240
14-12-2009, 08:34 PM
We are fitting the HP switch too control the condenser fan. When it reaches HP the fan comes on. The refrigerant is 134a. My engineer knows how to do it but he wants me to too set my own one up. Hes given me a comparitor and said find out how to set it up

Thanks

dougie
14-12-2009, 10:18 PM
Hi Deano, what you want to do is get an auto reset hp switch find out which of the two terminals have continuity across when required hp pressure is reached. wire the live to one side and the fan motor live to the other. hope this helps.

frank
14-12-2009, 10:25 PM
Will you be fitting an additional manual reset HP control to protect the compressor as well?

Brian_UK
14-12-2009, 10:28 PM
OK, find out what temperature you want the the condenser working at and set the fan control switch to that temperature.

Magoo
15-12-2009, 01:49 AM
Deano, ask your tradesman/ supervisor about this basic practice.