Hi,
(I'm french my english is bad)
We are building ice for show, we have alarm (E651) on our chiller and our compressor 2 is off.
I think we need password to reset this alarm.
I need password and to know how to enter it ..
Display is a CVM 20.
Maybe someone can be help us ?
Thanks !

Grizzly
07-12-2009, 08:50 PM
Hi,
(I'm french my english is bad)
We are building ice for show, we have alarm (E651) on our chiller and our compressor 2 is off.
I think we need password to reset this alarm.
I need password and to know how to enter it ..
Display is a CVM 20.
Maybe someone can be help us ?
Thanks !

Welcome groug.
Alarm E651 = Circuit 2 Safety High Pressure trip.
Manual reset necessary.
To clear alarms Press C2
This clears the alarms for Circuit 2.
C1 clears Circuit 1.
I hope this Helps? :D
Grizzly

groug
08-12-2009, 07:50 AM
When we press C2 alarm clear.. But when we press it again, alarm coming again and comp2 doesn't start.
Now glycol out : -2 and in : 0,5 cauz only comp1 is working..
We need comp2 to have -12 to make ice ..

groug
08-12-2009, 08:06 AM
We found, it's ok.
You can clear this thread :o

Grizzly
08-12-2009, 05:35 PM
Thanks!
It's OK!
No-Problem!
Grizzly