Hello everybody..
I am working in Oil & gas sector. We have a refrigeration compressor normally operating at suction pressure of 37/32 (Load/Unload) Kpa. What will be affect on compressor if i operate compressor on very low suction pressures??.. lets say on 15/10 Kpa..
I know it will enhance the condensate recoveries... but is it suitable for the compressor to operate it on very low suction pressures??
Please help me...
Regards

NoNickName
30-11-2009, 08:47 AM
Model of compressor and refrigerant?

coolerman
30-11-2009, 02:20 PM
ansar chiller manufacturer and compressör model ?

Ansar Iqbal
30-11-2009, 05:25 PM
Model: P200vl-he rotary screw compressor,2950rpm

refrigerant: Propane

refrigeration system was designed by propak..

Thanks for your reply nonickname and coolerman...

NoNickName
30-11-2009, 08:28 PM
Sorry, never heard of it.

RANGER1
30-11-2009, 09:38 PM
Ansar ,
You can't really damage a screw compressor by runing lower suction pressure .
It should have all its inbuilt safeties to protect it anyway .
It looks like a mycom compressor by the numbers you show .

The only thing that may be effected is oil and discharge temprature , depending what type of oil cooling .
ie water cooled , liquid injection .
Liquid injection would cover extra load .
Just run it at conditions you want and monitor pressures and tempratures to see what if any differences .

Does compessor have enough spare capacity to achieve suction pressure you require ?