PDA

View Full Version : Compressor Effieiency



ferret82
17-11-2009, 01:54 AM
I am wondering if there is any way you can test a compressor to see if it is functioning correctly. Not on the electrical side on the refrigeration side to see if it is pumping enough refrigerant though the system.

Hopefully i have explain this the correct way for you to understand.

Cheers

moideen
17-11-2009, 08:10 AM
I am wondering if there is any way you can test a compressor to see if it is functioning correctly. Not on the electrical side on the refrigeration side to see if it is pumping enough refrigerant though the system.

Hopefully i have explain this the correct way for you to understand.

Cheers


Compressor pumping test

connect a compound gauge with compressor suction pipe
close the compressor suction shut-off valve (should be very tight)
Link out L.P. control switch.
start the machine to pump down to below 24”Hg.
If at least 18”Hg not achieved think valves are defective.
If 24 Hg achieved stop compressor& monitor vacuum rise rate. Normal criterion for a new/re-manufactured compressor is not more than 10”/minute.

(This is only for reciprocating compressors)

Moideen-Dubai

ferret82
17-11-2009, 08:14 AM
Thanks for that information, Very handy this site:)

lowcool
17-11-2009, 11:19 AM
checki manufacturers ratings.24 inch is a bit low for me if its hermetic.