Hi
I want to design a Heat Exchanger i.e. Condenser .

Subcooling is 8.3 K
Condensing Temp 54.4 Deg C
Ambient Temp is 38 Deg C

So Temp Difference is (54.4-8)-38=8.4 Deg C
Heat Rejection is 13.5 KW.
Copper Tube OD is 3/8" and Thikness is 0.08mm.
Fan air flow is 1.44 m3/s at 50kpa Pressure Drop .
Tube Triangular pitch is 25.4 mm
and Horizontal pitch is 22 mm.

Please suggest How can i get U value for this .

desA
11-11-2009, 12:45 PM
Visit the CoolIt software site & purchase their condenser design program. http://www.coolit.co.za/software.htm

It's excellent & doesn't cost much at all.

amitsaxena
11-11-2009, 12:57 PM
Sagar the data u hv provided is not sufficient as

1. Nos of rows and column
2. Refrigerant

Provide more data

Thanks
Amit

sagar45
12-11-2009, 09:22 AM
No.of rows are 4 and Refrigerant is R22

amitsaxena
12-11-2009, 10:25 AM
What about columns?

gmavrom
29-05-2010, 04:57 PM
let's say that the number of columns is 3 how is the U value calculated?