We have designed Deep freezer using cascade system. Primary uses R 404 and secondary uses R 23 . After 2-3 Months working temperature increases tp -55 degrees. What will be the problem. Pls advise.

rizwankhan
10-11-2009, 12:01 PM
couple, you used refrigerant both together R 404 & R 23 ? quote head pressure,suction pressure, fixed txv or capilary tube

NoNickName
10-11-2009, 12:41 PM
What is tp? Evaporating temperature of the low stage?
How is the system? DX? Pumped liquid?

D.D.KORANNE
11-11-2009, 09:13 AM
Look for the oil build up in low side r-23 evaporator . Probably you are operating at say -60 deg c or so the critical issue is the oil return . Although you would have used oil separators for r-23 , these are 80-85% efficient. Hence the oil carried over forms a film inside low side evap and efficiency drops . Another area is the quality of oil with r-23 ,it has to have a pour point lower than the design evap temp ( for r-23) . The oil solidifies and fails to return to compressor. For efficient oil return use of borosilicate microfibre with an efficiency of 99.999% would address the oil issue .

D.D.KORANNE
11-11-2009, 09:15 AM
for further interaction send a PM : ddk0123@gmail.com

R. skiffington
12-11-2009, 09:23 AM
Probable case of oil logging, significant ice build up in freezer? leave off for a couple of days and restart. How old is the system? has it had other problems? Has it been operating 2-3 months from new? Hard to work with such little info.