i have 2 chillers both going out intermittantly 1 on 61 and 46 faults and the other on 48 and 57, i have found the the oil heater on the second unit to be open circuit, has someone got a manual or any ideas?
i have found the pressure transducers to be a little out of calibration but i have not got the service code to get into the Pro Dialog Plus controller to recalibrate these.
the sensors appear to be ok
thanks

Brian_UK
09-11-2009, 05:19 PM
You can also get Carrier literature from here..

http://eto.carrier.com/lit.asp

boxhead1976
10-11-2009, 11:27 AM
Thanks BrianUK your a champion!!

boxhead1976
11-11-2009, 10:15 AM
Thank you Narcom you are also a legend

Peter_1
03-12-2009, 08:05 PM
If the oil heater goes erratic on some Carrier chillers on the master compressor, then the whole unit is shut down.

Pauly.
06-07-2010, 06:10 AM
gdya brian my name is paul im a mechanic in the ACT australia ive read a few of your posts thanks for sharing your knowlege. Ive found a programmable carrier tstat that is melting itself off the wall! its 24v and all the obvious things have been done (including running new cable to the tstat), the unit has gone threw 2 commpressors already in the last 5 years. The utec board outdoor seems ok i never replaced one in my ten years at carrier.