View Full Version : R507 instead R404a?
Friobernal
29-11-2004, 07:42 PM
Hi,
I´ve heard that R507 is a better refrigerant than R404a, and it is going to substitute R404a because R507 was patented some years ago?
Some comments...?
chemi-cool
29-11-2004, 07:47 PM
Just between the two of us, when ever any unit works on 507 brakes, I change it back to 22. ;)
From that moment it works better.
No, I didnt hear such a thing.
Chemi :)
The two refrigerants are almost identical. Essentially, if you take R507 and add a small amount of R134a, it becomes R404A.
chemi-cool
30-11-2004, 07:28 PM
Hi Gary,
True but 507 has a slight higher pressure on condensing,
still they are not as good as 22.
Chemi :)
coolkev
30-11-2004, 07:54 PM
:cool: I agree with gary they are all most identical even the price is almost the same. I disagree with R22 being better. There also about the only refrigerants that are ok to mix in a system. I have always disliked R22 especially in low temp applications.Having to run head cooling fans and on s'market rack systems desuperheating TX valves on the suction header. On medium temp care must be taken to ensure low superheat or discharge temps go off thier face. I still think R22 is still for air conditioning. R404a and R507 are long term replacements for good old R502 with the use of POE oil. Regards Kev
chemi-cool
30-11-2004, 08:21 PM
Hi Kev,
I use 22 for years for AC and low temp down to -18 freezers.
No problems at all, no head cooling fans (its hot over here)
In new freezers, I have sterted to use R404.
Chemi :)
Hmmmmm...
R134a is not a blend, and therefore cannot separate.
IIRC, R507 is a near azeotrope. Adding a little R134a to it, making it R404A makes it a zeoptropic blend, thus the R134a can separate where there is a saturated mixture, but will blend back together everywhere else in the system. Fractionation inside the system is not a problem.
As I understand it, the biggest problem with the new refrigerants is POE oil. It is not only hydroscopic, but highly detergent as well.
I don't know anything about the world bank, nor do I care, but the ozone depletion farce was pure BS, and I will never forgive the EnviroNazis for screwing up my industry. They took the joy out of my job. The only group that makes me more angry is the TobaccoNazis.
chemi-cool
01-12-2004, 04:05 PM
Funny Gary but I know exactly how do you feel ;)
Chemi :)
coolkev
01-12-2004, 09:55 PM
:cool: Gary i agree the ozone buisness is a crook off s h i t . Didnt it come at the same time as duponts patents on ***** run out? And as i understand it dupont was the main company backing the ozone theory or am i just suspicious?
shogun7
02-12-2004, 01:07 AM
Has anyone used Icors NU-22
NU-22 is the most practical and natural choice for the replacement of HCFC-22. It is the only HFC based R-22 replacement that is compatible with synthetic and mineral oils (MO,AB,POE). NU-22 has also proven to be compatible with all standard equipment components and materials used in R-22 manufactured systems. After conducting over one thousand hours of compressor wear testing, NU-22 has proven to be fully suitable for use in scroll, screw, rotary and reciprocating compressors. :confused:
R507 is a near azeotrope
R507 is an azeotrope (not a near azeotrope).
All R500 numbers are azeotropes. :rolleyes:
frank
02-12-2004, 10:24 PM
Has anyone used Icors NU-22
Can't say I've heard of it Shogun
Is it available in the UK or just Stateside?
shogun7
03-12-2004, 03:59 AM
Can't say I've heard of it Shogun
Is it available in the UK or just Stateside?
Frank, I believe it's only avialible in the US and Canada...you can read more about it at:
http://www.tropicsupply.com/RefrigerantsicorNU22.htm :o
Frank
Its available from klea as AZ50.
I don't know anything about the world bank, nor do I care, but the ozone depletion farce was pure BS, and I will never forgive the EnviroNazis for screwing up my industry. Gary
I said this many times before.............Next time some bald headed, bearded, , white coated , university lab closetted scientest, comes up eith a theory and blurts out,
" the temp of the world is rising.................The ice caps are melting........... We BLAME CHLORINE..................Lets go look for chlorine........."
.
They found it, it was a constituent of refrigerants...........or solvents as they were fond of calling it.
Who was blasting tonnes of the stuff every day..............Yes , mainly R11 as a cleaner.
The Tobacco companies used it to " fluff" up the tobacco, blasted hundreds of tonnes into atmosphere every day
The Pcb , chip electronic manufacturing companies. To clean electronic components. ( Silicon Valley)
Aerosal companies who filled cannistors with it.
Like with all other issues, they could have stopped these industries using refrigerants............
No , they developed a whole new host of refrigerants
We , refrigerant people had no voice...........we sat back glumly and took it on the chin...................
It says a lot about us.............
Look at the hunting ban here..............Do the Country Alliance sit back ??? No they dont..............They fight back for what they see as their right to kill poor little fox.
I by the way do not agree with killing animals for sport, wether it is a fox in an english meadow, or a Rich Yank paying his green dollar to down a magnificent lion..............or giraffe..
They is always a solution to things..............Solutions are destroyed when money aspects override the issues.
The chemical companies saw an opportunity to make big money.........
Who said it was Dupont ?? who supported the idea..........If is is true we can start by stop buying dupont refrigerants.......
I did try and found out R507 works better then R404a
chemi-cool
08-12-2004, 07:34 PM
Hi Jay,
Good to see you here. :)
Better in what? AC or refrigeration med, or low temp?
Chemi :)
RogGoetsch
09-12-2004, 07:58 AM
I said this many times before.............Next time some bald headed, bearded, , white coated , university lab closetted scientest, comes up eith a theory and blurts out,
" the temp of the world is rising.................The ice caps are melting........... We BLAME CHLORINE..................Lets go look for chlorine........."
Actually, chlorine was fingered for the ozone hole, not global warming.
Perhaps the hole is a naturally occurring phenomenon, but the truth is we were pumping billions of tons of crap into our atmosphere. I was skeptical of the science until I read a pretty understandable paper which convinced me it was too probable to ignore.
Pollution is one of the things we humans do best. Denying that we are poisoning ourselves is probably the second. Look at all the epidemics in all the cities of the world before sanitation. We used to dump our sewage in the streets, let it run into the rivers. Downstream cities drank it.
We , refrigerant people had no voice...........we sat back glumly and took it on the chin...................
It says a lot about us.............
I think it says we care more about the health of the planet than our own convenience.
They is always a solution to things..............Solutions are destroyed when money aspects override the issues.
Another word for it is self-interest. We all have a hard time seeing beyond our own. It's why our world is the way it is. We live in an amazing paradise: incredibly beautiful in every way, food grows from the earth itself or falls from the trees. But we only see the worm in the apple or decide we don't have enough.
The chemical companies saw an opportunity to make big money.........
And then orchestrated an international conspiracy in which they enrolled scientists from around the world to create a bizarre theory? And not a single conspirator blew the whistle, and they all either did it for no personal gain or else the secret payments from the chemical companies were never discovered?
Hmmm. I either need more details of this amazing conspiracy or send me some of that stuff you're smoking, Dude!
Relax. Life is short and most of it can be pretty good if you can get your attention off whatever it is you love to bitch about!
Rog
And then orchestrated an international conspiracy in which they enrolled scientists from around the world to create a bizarre theory? And not a single conspirator blew the whistle, and they all either did it for no personal gain or else the secret payments from the chemical companies were never discovered?
Hmmm. I either need more details of this amazing conspiracy or send me some of that stuff you're smoking, Dude!
Rog
Dont be so daft and condesending Rog..............use your bottle
You dont need to " muster" opr mobilise a coalition or alliance in order to "conspire"
You need an army of sheep..........
Youre a typical American.........
RogGoetsch
09-12-2004, 05:02 PM
Dont be so daft and condesending Rog..............use your bottle
You dont need to " muster" opr mobilise a coalition or alliance in order to "conspire"
You need an army of sheep..........
Youre a typical American.........
Sorry if I sound condescending, Abe. I come from a country where the President can't get a blow job from an intern without the entire world knowing about it! Conspiracy theories don't hold much water with me. Like Occam's Razor, the simplest explanation is probably the most correct.
I think the industry might have done more to oppose the change except that everyone above the tech level saw the profit potential in the change, and only the techs feel the pain.
Rog
chemi-cool
09-12-2004, 05:23 PM
Hi Rog,
Its not only the techs pain, its the simple problem that no one was able to bring any proof so far!
Al we've heard in the past ten years was, bla, bla, bla.
But try to to find the bank balance of Dupont for example,
I'm sure you will see a sharp curve upwards of the income, baseb on what we call over here, Got the customers by the balls.
Can any one afford not to pay the price?
I'm only making money out of it but I feel i'm cheating on my clients :(
Chemi :)
Conspiracy theories don't hold much water with me.
Rog
Hey Rog,
I blurted out my response this am...........but glad to receive a response from you.........Now lets get this straight.........
Who said anything about a conspiracy ????? Did I say it ????
Or did you make it up..........or go on the defensive.........as you guys are prone to do......... :D
What Im referring to is the way Big Business operates...............anywhere in the world.
Businesses need to launch new products , new models, new technologies............new software..........incorporate a few changes, jazz things up, in most cases we do benefit from better more efficient products..........
So , tis no conspiracy...........tis business. Thats the way of the world.
I did slip up on the global warming ...............it was that darn hole in the sky and people fearing about getting more skin cancers.......... Thanks for pointing it out.
But you ignore my argument about Industry who vented hundreds of thousands of cfc's into atmosphere............Not fridge techs.......
A better solution would have been to analyse usage..........bring in controls, licensing and methods..........yes, recycling and all that crap..........
Not wholesale elimination............
Hence, my prognosis that it was engineered by big business for monetary gain................and that is my view...........everybody can make their own minds up.......and I will encompass all views or opinions............
And I promise..............I wont accuse you of being high on dope if your opinion differs from me.......... :)
Since you guys are so concerned about environments.............how about your lobbying your legislator to sign up to Kyoto!!!
:D
Adieu Bud...........Have a great day...............
Abe
Servicefrigo
09-12-2004, 08:46 PM
HY.
I Prefer R 507 because, I ask you what hapen*t when you lose 20% of a charge R 404 a . Is the same when you lose 20%
of R 507.what* s your opinion.
Occams Razor
Occam's Razor (also Ockham's Razor or any of several other spellings), is a principle attributed to the 14th century English logician and Franciscan friar, William of Ockham that forms the basis of methodological reductionism, also called the principle of parsimony.
In its simplest form, Occam's Razor states that one should not make more assumptions than needed. When multiple explanations are available for a phenomenon, the simplest version is preferred. A charred tree on the ground could be caused by a landing alien ship or a lightning strike. According to Occam's Razor, the lightning strike is the preferred explanation as it requires the fewest assumptions.
http://en.wikipedia.org/wiki/Occam's_Razor
I picked up the definition from link above.
Marc, are there no limits to your knowledge and brilliance ???? :)
RogGoetsch
10-12-2004, 02:12 AM
You mean that the hole might be natural is likely more correct?
Ooooh, good one, Marc! Could very well be.
Rog
RogGoetsch
10-12-2004, 07:16 AM
Who said anything about a conspiracy ????? Did I say it ????
Or did you make it up..........or go on the defensive.........as you guys are prone to do......... :D
Yeah, and you know what we do when we get defensive! Besides, I’ve heard you guys have WMD’s (Weapons of Mass Destruction), so watch it!
What Im referring to is the way Big Business operates...............anywhere in the world.
So , tis no conspiracy...........tis business. Thats the way of the world.
But you ignore my argument about Industry who vented hundreds of thousands of cfc's into atmosphere............Not fridge techs.......
A better solution would have been to analyse usage..........bring in controls, licensing and methods..........yes, recycling and all that crap..........
Not wholesale elimination............
Hence, my prognosis that it was engineered by big business for monetary gain................and that is my view...........everybody can make their own minds up.......and I will encompass all views or opinions............
Abe, conspiracy just means two or more agreeing, usually in secret, to do something, usually wrong. For business to “engineer” the change would mean more than one person agreeing to make it happen. That’s all a conspiracy is.
Your solution makes too much sense to actually be agreed to by any governing body I’ve ever heard of. I think it was only fear that motivated the world community to come together on this, and fear, while an effective motivator, does not care for fine distinctions.
Perhaps we could have made an exception for refrigeration use, but in one discussion I read in the early days of the debate, it was generally accepted that most refrigerant would eventually leak out, no matter how good the regulations and practices, since that’s what old systems do.
Besides, everyone thinks his use is critical and should be the exception. Emotionally we’re still children. “If I can’t have it then neither can you.”
And I promise..............I wont accuse you of being high on dope if your opinion differs from me.......... :)
Please. Here in California we refer to it as “medical marijuana” and everyone has some in his medicine cabinet. As a matter of fact, I think my back is going to feel sore in a little while….
Since you guys are so concerned about environments.............how about your lobbying your legislator to sign up to Kyoto!!!
What?! And offend our biggest polluters…er, ah, I mean political contributors… no, wait, I mean industries? We’ve got the best democracy money can buy and as long as it stays bought, we don’t have to worry about little things like breathing or getting along with the rest of the world. And global warming concerns are for people without air conditioning!
Rog
RogGoetsch
10-12-2004, 07:39 AM
Its not only the techs pain, its the simple problem that no one was able to bring any proof so far!
Al we've heard in the past ten years was, bla, bla, bla.
Chemi:
(Ozone depletion by chlorine is a theory, hence not provable, but possibly disprovable. Theories explain observable phenomena and allow us to make predictions. If a prediction fails, then the theory needs to be revised or discarded.)
Can any one afford not to pay the price?
I'm only making money out of it but I feel i'm cheating on my clients :(
Chemi :)
I understand your frustration. I, too, frequently feel embarrassed when I hand the customer the bill. The refrigerant prices are outrageous, yet I still feel I have to mark up 50% to cover warranty if it leaks. How much mark-up do you use?
Rog
Rog
So at the end of it.............You back track and end up agreeing to everything I said...............So your argument was a total waste of
Y(our) time............
Sheesssh............whats the point ?????
In future Ill try avoiding talking to brick walls........
Thom101
10-12-2004, 11:32 AM
[QUOTE=RogGoetsch]Chemi:
(Ozone depletion by chlorine is a theory, hence not provable, but possibly disprovable. Theories explain observable phenomena and allow us to make predictions. If a prediction fails, then the theory needs to be revised or discarded.)
Theory? more like fact mate. you never study chemisty? when you mix CFC's with O3, the chlorine in them strips away O1 molecules from the O3 one atom at a time. hence ozone depletion. unless you can prove me wrong?
chemi-cool
10-12-2004, 02:15 PM
So guys, it looks we will argue about the demage of refrigerants for many years to come or to be more presice, untill a new generation of techs, born after 1993 ( they are 11 now) wiil take the lead and r-12,22,502 will only be part of our history.
Theory? more like fact mate
So, wise guy, how much R-12 realesed in london, you will need to create a hole 1 sq/m over New-Zealand??? :D
But this is not the issue, it is the global worming.
And there, the only factor is MONEY!
I’ve heard you guys have WMD’s,
Please Rog, for those who did not speak English at birth, explane WMD.
Chemi :)
chemi-cool
10-12-2004, 02:16 PM
So guys, it looks we will argue about the damage of refrigerants for many years to come or to be more precise, until a new generation of techs, born after 1993 ( they are 11 now) Will take the lead and r-12,22,502 will only be part of our history.
Theory? more like fact mate
So, wise guy, how much R-12 released in London, you will need to create a hole 1 sq/m over New-Zealand??? :D
But this is not the issue, it is the global worming.
And there, the only factor is MONEY!
I’ve heard you guys have WMD’s,
Please Rog, for those who did not speak English at birth, explain WMD.
Chemi :)
chemi-cool
10-12-2004, 03:15 PM
Thanks Marc. ;)
Chemi :)
RogGoetsch
10-12-2004, 04:55 PM
Rog
So at the end of it.............You back track and end up agreeing to everything I said.....
Not really. I think we had to go ahead with the chlorine elimination as the safest approach given the data available and the slim chance of a consensus around any alternative.
I also think it is a colossal waste of time and energy to bitch about it. :)
Rog
RogGoetsch
10-12-2004, 05:05 PM
Theory? more like fact mate. you never study chemisty? when you mix CFC's with O3, the chlorine in them strips away O1 molecules from the O3 one atom at a time. hence ozone depletion. unless you can prove me wrong?
The theory part is that this observable chemical behavior is occurring at high altitude with chlorine stripped from refrigerant molecules that are themselves quite a bit (4X?) denser than air molecules (O2 & N2); and that the hole we observe occurring without historical measurements to compare with, is not a naturally occurring phenomenon, but the result of this chemistry.
Rog
RogGoetsch
10-12-2004, 05:40 PM
Please Rog, for those who did not speak English at birth, explane WMD.
Chemi :)
Sorry, I must be overmedicating again!
After this election, WMD has become a mantra over here. “Weapons of Mass Destruction,” also known as “Weapons of Mass Distraction” to those of us who think our leadership may be not wanting us to look at their whole record.
WMD is stuff Britain and Europe have to assure themselves that the USA can never attack them. The USA would never attack a ligitimate force, they only ever take on straw men, country's that they know don't have WMD even if WMD is used as an excuse for attack :)
Yeah, well don’t be too sure! Remember we can still muster a powerful coalition including umm, er, any country who will even talk to us in a few years!
Rog
jsugalski
04-01-2010, 02:07 AM
Hmmmmm...
R134a is not a blend, and therefore cannot separate.
IIRC, R507 is a near azeotrope. Adding a little R134a to it, making it R404A makes it a zeoptropic blend, thus the R134a can separate where there is a saturated mixture, but will blend back together everywhere else in the system. Fractionation inside the system is not a problem.
As I understand it, the biggest problem with the new refrigerants is POE oil. It is not only hydroscopic, but highly detergent as well.
I don't know anything about the world bank, nor do I care, but the ozone depletion farce was pure BS, and I will never forgive the EnviroNazis for screwing up my industry. They took the joy out of my job. The only group that makes me more angry is the TobaccoNazis.
so do you also hate the feminazis? :)
so do you also hate the feminazis? :)
Yep... and just so you don't get the wrong impression, I don't like the conservatives, either.
The thieves and dictators versus the dictators and thieves. Politicians are the scum of the Earth.
jsugalski
04-01-2010, 02:54 AM
Yep... and just so you don't get the wrong impression, I don't like the conservatives, either.
The thieves and dictators versus the dictators and thieves. Politicians are the scum of the Earth.
fair enough, just the "nazis" part of your phrases prompted me to ask even if in jest...anyway I'll leave the politics for another time, that problem I had with the phase change unit in another thread, I do have a relevant bit to ask in this thread, I was considering getting a danfoss compressor to replace it on ebay, especially if it goes for as little as it is currently going for...it's a SC12CL R404A/R507 whereas the one I have in the unit is the stock nf9fx danfoss that is in it that I suspect has issues...I may have it fixed anyway, but the sc12cl uses better coolant either 404 or 507 depending on if this person refilled it vs the 134a in my current unit, as well as a slightly bigger motor so I should get better temps overall...just wondering what your opinion is on this.
jsugalski
04-01-2010, 02:56 AM
so in this case, it's not 507 vs 404, it's 134a vs 507/404 lol
asproegypt1
03-03-2010, 03:41 PM
Hi
I was searching for anything to re-charge my R-123a So I found Something Maybe It Will Be More Useful For Your Issue And
otherwise it helps me too
rizkbrothers.com/Arabic/products.php?tn=cHJvX3Byb2R1Y3Rz&for=Mzk%3D&main=0&sub=0&pro=39&lan=Ar
muddassarusa
14-06-2010, 08:25 PM
The two refrigerants are almost identical. Essentially, if you take R507 and add a small amount of R134a, it becomes R404A.
Hi Gary,
what % can be mix with R-507 and R134a become correctly as R-404a? 10% or 20% or???
CPboy
20-07-2010, 04:56 AM
please correct me if i'm wrong,
r507 and r404 is better for low temp applications than r22, my experience with r22 especially in our hot tropical climates is that the compressors bruns out faster than r404a/507 compressors,
but 1 thing why i like r507 more than r404a is when you have a leak, r507, you can just refill the syatem after fixing the leak while r404a, you will have to drain all refrigerants and refill it because if youjust add it, the blend will not be perfect anymore for r404a....
Gerrit
20-07-2010, 07:04 AM
Hi Gary,
what % can be mix with R-507 and R134a become correctly as R-404a? 10% or 20% or???
R404a
44% of R125
4% of R134A
52% of R143A
R507
50% of R124
50% of R143A
oldesky
21-07-2010, 05:20 AM
On low temp R507 is better than R404a. It is considered azeotropic because it has a temperature glide less than one degree. Tests done on partially replacing the R404a system charge at various percentages with R507 show little or no decrease in efficiency and in some cases an increase. R507 can be vapour charged which can be an added advantage.R22 is not as good at low temp especially on systems with higher than normal return suction temps due too high discharge temperatures. R134a is the best option for medium temp refrigeration and R22 will soon be phased out in many countries that havent done so already. I agree with you on R507 Gary but strongly disagree on Tobacco. As an asthma sufferer whos Asthma is triggered by cigarette smoke, I dont believe that smokers have a right to give me an asthma attack.
I agree with you on R507 Gary but strongly disagree on Tobacco. As an asthma sufferer whos Asthma is triggered by cigarette smoke, I dont believe that smokers have a right to give me an asthma attack.
It might interest you to know that I was an early advocate of non-smoker's rights. But somewhere along the way I realized that there was no quid pro quo, that non-smokers didn't give a damn about smoker's rights.
If non-smokers don't care about my rights, then why should I care about theirs? If they think it's okay to rob me, then why shouldn't I blow smoke in their faces and watch them choke? Seems fair to me. I'm choking on their taxes.
lawrence1
22-07-2010, 12:29 AM
Interesting comparisions link below.
www.solvay-fluor.com/.../r507_in_comparison_to_r404a_and_practical_experiences.pdf -
oldesky
22-07-2010, 02:40 AM
Gary whilst I greatly respect your refrigeration opinion, I disagree with you on tobacco. In saying that I do agree that you have a right to commit suicide as quickly or as slowly as you wish,as long as you dont kill or injure others on your quest.but this is a refrigeration site so I will not continue a fruitless and pointless argument.
paul_h
22-07-2010, 09:36 AM
^ you just did :eek:
skoerper
19-01-2011, 05:51 AM
Have you tried R407A?
It's a proven replacement in exsiting R22 low and med temp refrigeration equipment. No equipment changes or mods. Does require at least 50% POE.
Copeland, Carlyle and Bitzer approved.
Walmart, Food Lion, Costco, and many others are using it in new equipment since it has a low GWP compared to R507 and R404a.
Horoaffonee
09-04-2011, 12:42 AM
I would like to know if i can use the Microchip 25lc320 instead of the Atmel AT25320the datasheet looks like similary.Or maybe is there a equivalent by Microchipthank you
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.