04-11-2009, 02:29 AM
Hello,
I am looking for help sizing an expansion tank for a chilled water system. It is an exsisting system and I don't know exact fluid content. Do I need to do a dilution test to get a accurate messurement. Can I just overestimate?

Sridhar1312
04-11-2009, 03:34 AM
Expansion tank shall be kept at topmost level of the chilled water circuit.ideally it is better to calculate the total holding capacity of circuit .As a rule of thumb around 3% of the flow rate is adequate for expansion tank if it is chilled water system

Brian_UK
04-11-2009, 09:21 PM
Document here has tables and calculations for sized expansion vessels.

http://www.mikrofill.com/images/PDF/n-and-de-range.pdf

nike123
05-11-2009, 09:17 PM
Here (http://www.reflex.de/reflex/pdf_engl/REFLEX_EN.exe) is software for such calculations.

Helper monkey
16-11-2009, 02:27 AM
THANKS Guys knew you could help