21-10-2009, 05:10 PM
would like to know how to chang temperature setting on serve over display cabinet,buttons at left hand are arrow pointing upwards and arrow pointing downwards,at right arrow pointing straight right and snowflake symbol.Problem is drip tray at top is freezing solid then overflowing.Thanks

Brian_UK
21-10-2009, 11:02 PM
Any name on the display itself?

LAE, Eliwell, Dixell etc

folco
22-10-2009, 05:51 PM
Frilixa,But that could be seller rather than manufacturer

Magoo
22-10-2009, 10:56 PM
Folco.
sounds like the condensate drain is blocked, and if icing drain tray up, then set point on chiller is too cold.
Does controller have a set button?.
try www.frilixa.com (http://www.frilixa.com)

folco
23-10-2009, 06:10 PM
no set button,just buttons as described in previous post.thanks for reply.

Magoo
24-10-2009, 12:21 AM
Hi Folco.
Sounds like a re-badged Danfoss EKC controller, but then I could be wrong, quite often the case.
Did you try and clear the condensate drain?.
Did you check the web site suggested?.
Try and hold both up and down arrows at same time for period of say 5 seconds, and what happens.

folco
24-10-2009, 05:36 PM
yes,cleaned out drain hole.Will try holding both buttons,thanks for your help.PS bottom setting at 4 degrees,top at 6,is this ok?

Magoo
25-10-2009, 01:10 AM
Hi Folco.
sounds about right, could be a case that the controller relay has failed closed and keeping the unit cooling, hence freezing problem.
I will see if I can find and send to you a set-up brochure. Can anyone else help with this, open question.
martin

folco
25-10-2009, 05:34 PM
does go off and into defrost mode then back on regularly

folco
30-10-2009, 06:04 PM
holding buttons for 5 seconds worked ok.thanks for info