Hi all,

Some advice. I have a Fujita A/C which runs fine on the cooling cycle, but on heating the condenser fan starts up then the indoor fan runs for a few seconds and then cuts out. Any ideas as to the cause? The unit was recently vacuumed and recharged and the filters have all been cleaned after which it ran fine for abpout a day but it is cycling again. No signs of any leaks in the system or faults with the compressor, etc. When it was first serviced the port pressure was around 2,000 kPa but it now cuts off at just under 1,600 kPa.

Thanks for any suggestions.

superswill
21-10-2009, 01:48 AM
indoor coil sensor?

do you have a model number and fault code and flashing light sequence?

paul H on here is very good on fuji and from your part of the world