2 off evaporators in same room running off same system . Each has its own TX valve and distributor :D.
note has other units as well on this system .:D
Suction lines off each evaporator go back to common suction header .:D
Someone has piped up a hot gas defrost system to it as its a 0 deg C room:D
Common hot gas line with 1 solonoid feeding hot gas into each evaporator at same time between TX valve and distributor ( no non return valves on each unit of hot gas line ) .:rolleyes:
Suction line of each evaporator has gas powered solonoid with hot gas pressure regulator piped around it.:D
The TX valves can't work properly can they ?