PDA

View Full Version : Total Heat Rejection



schquenz
06-10-2009, 03:11 PM
Someone can help/guide me how to calculate the heat rejection for Air-cooled chiller.

Brian_UK
06-10-2009, 08:50 PM
Umm, cooling load plus motor power if in circuit.

frank
06-10-2009, 11:39 PM
The heat rejected at the condenser will be equal to the heat absorbed at the evaporator plus the heat of compression, if the system is in balance.