Can you help me I have some early Carrier Maxima,Maxima2 which are running on R22
Is there a drop in replacement or have i got to change alot of parts?

absolute-zero
04-10-2009, 06:57 PM
Hi Guys
Can you help me I have some early Carrier Maxima,Maxima2 which are running on R22
Is there a drop in replacement or have i got to change alot of parts?

How about refrigerant HFC 407c. You will need to change the oil to a POE as well change the drier. This refrigerat has simliar characteristics and temp glides those of R-22 and its ozone friendly.

A-Z

hyperion
05-10-2009, 12:56 PM
Go for R417A. Measure the quantity of R22 that you remove from the system, uif the system has a drier it would be best to change this, vac it out and then add between 90 and 95% by weight of R417A. System should work with very similar pressures and temperatures to R22. No need to change the oil or any controls, TXV etc.

tspgr
05-10-2009, 01:11 PM
Hello Andy

You can change R22 with a lot of new refr. but if we are talking about an international transport unit I suggest to make it R404.
more work must be done in the refrigeration circuit but if the customer have a breakdown in an other country than yours it will be more easy to be repaired.

Mike

pina
05-10-2009, 03:54 PM
:off topic:Sorry I´m from Brazil. Can you help-me ? I started one system cascade 404 # 1st and 744 # 2st, but I need to know if can I used compressor bitzer IV to do it?

abbsnowman
06-10-2009, 06:29 AM
Just a couple of points here.
-Why are we changing away from R22 again?
-Second, changing the oil is never a bad idea under any circumstances in my opinion.
-Changing to R404A requires TVX replacement and heat exchanger. (May also require software update in some cases.)

Last and not least, I have no idea what the last post means? LOL

tspgr
06-10-2009, 01:33 PM
Just a couple of points here.
-Why are we changing away from R22 again?

good point but if he wants to do it ok


-Second, changing the oil is never a bad idea under any circumstances in my opinion.

you are right but you must clean the circuit


-Changing to R404A requires TVX replacement and heat exchanger. (May also require software update in some cases.)

you are right about the TVX but for the maxima I dont agree for the heat exchanger because you have the subcooling condesen that helps you .





Last and not least, I have no idea what the last post means? LOL

I don't understand ither

abbsnowman
07-10-2009, 05:53 AM
I don't recall ever seing a 404A system with no heat exchanger???

tspgr
07-10-2009, 10:04 AM
I don't recall ever seing a 404A system with no heat exchanger???

I dont understand you.
maxima R22 has a heat exchanger ????

abbsnowman
08-10-2009, 05:43 AM
Sorry, I was not aware of that. Here in North America the units are a bit differant.
Hope I helped more than I confused.

Boss302
08-10-2009, 06:23 AM
Here in North America, R22 isn't hard to come by or expensive. Maybe it is different elsewhere. Here, I can't see any reason to convert an R22 unit.

hyperion
08-10-2009, 08:04 AM
R22 is not too expensive in the UK at the moment, but once we only have reprocessed R22 available, the chemical companies will be able to charge whatever the wish. It will not be governed by what the industry can afford more likely to be on a supply and demand basis. They will have the limited supply and we will have a larger demand. As yet there has been no indication at to what price level may be enforced.

MRW
13-10-2009, 11:02 PM
Another drop in replacement for r22
is r422d,dont know alot about it but came across it in a Dawson cold store that had been on r22

lowcool
14-10-2009, 12:15 AM
r422d is a low/medium temperature replacement and not sufficient for capillary systems.417 is not suited for low temp applications

ekosuranto
21-10-2009, 09:46 AM
hi guys,

can you help me to take a software for calculate BTU/hr for transport air conditioning ?

thx bro

sedgy
21-10-2009, 05:46 PM
why change from r22=
ask the polar bears , have you not heared ?

abbsnowman
21-10-2009, 09:38 PM
Point taken there Sedgy! ;)