02-10-2009, 06:27 AM
Hi All

have a question would like to know if anybody has ever used PPR pipes for Chiller installation instead of the normaly used Steel pipes and what is the outcome can they be used or not, this just for info only have not used anywhere but just need the knowledge for future reference.

nike123
02-10-2009, 11:45 AM
I use it on few sites without any problem. Just make sure that is composite, faser-composite type or special as this one (http://www.aquathermpipe.com/climatherm-overview.html).
That is because of thermal stretching of pipe which is high for normal (no composite). Stretching of composite pipe is comparable with steel pipes.
Fittings are same.

Meer Abdulrehma
16-10-2009, 05:47 AM
Hi thanks for the above info in comparison to the schedule 40 how is the condensation