PDA

View Full Version : Mitsubishi PUH-10YD



Slim R410a
21-09-2009, 03:22 PM
Hi Guys,

Would anyone quickly be able to tell me the exact nominal and UK cooling capacities of this outdoor unit?? R407c, the labels on the outdoors were worn off by the sun. Guessing somewhere around 25kw nominal??

Cheers,

Thermatech
21-09-2009, 07:33 PM
I think the PUH 10YD was the old R22 system. The outdoor unit was the old City Multi chassis with 4 fans.
With the PEH YD ducted indoor unit nominal UK cooling was 24.44 kw but you could also install as multi split with up to 3 Mr Slim indoor units.

The R407c system was PUH P10YE
with outdoor unit in City Multi single fan chassis.
The UK nominal cooling was 25.2 kw with the ducted indoor unit PEH P10YE
or up 4 mr Slim indoor units

Info from archive 2001 catalogue

Slim R410a
22-09-2009, 06:50 AM
Yes they are definitely the single fan chassis, (same as vrf) 4 exactly the same each connected to a single high static ducted unit. The only way they are linked is using 2 controllers rather than 4.
Someone had written in marker pen PUH-10YD, and i could just make out the R407c on the plate.
I just have to replicate the 4 systems with 4 new on another site so will go for 4No. PUHZ-P250's and 4No. PEA-RP250's (uk cooling range upto 25.75kw)
Thanks for the info,

Thermatech
22-09-2009, 01:34 PM
These systems were always extra large Mr Slim split systems so you can group control multiple systems from one remore controller if you want the same as any Mr Slim systems.