PDA

View Full Version : R410a evaporative condenser



Lc_shi
17-09-2009, 06:39 AM
Hi sirs

is there any manufacturer producing r410a evaporative condenser ? it it better performance than R22 one? hope somebody can help me about it. thanks in advance!


regards
LC

elliswyatt
09-12-2009, 02:46 AM
I don't know of any; I think the pressures of R410A may be too high. Might check with Recold.

Magoo
09-12-2009, 02:56 AM
So long as it rated for operational pressures, where is the problem. Total heat of rejection is the primary factor.

US Iceman
10-12-2009, 12:35 AM
The manufacturers should be able to give you a correction factor for R-410a. Since they already have R-22 ratings I suspect the correction factor would be based on the R-22 data.

I looked at this one time. R-410a looks like a good refrigerant except for the high pressure. If you use a lower condensing temperature you should be below the manufacturers maximum pressure rating.

Darrbaby
13-12-2009, 12:47 AM
Dont use an r-22 coil, there rated at 300 psi. 410-a is rated to 450 psi. on residental and most light commerical package units as well. Hope this helps.

Darrbaby
13-12-2009, 12:49 AM
Oh most manufactures have coils rated for both but you need the correct txv.

US Iceman
13-12-2009, 05:40 PM
The condensing temperature/pressure will determine the required design pressure. If it's air-cooled then the design pressure would of course be much higher.