PDA

View Full Version : Maximum discharge pressure ZB scroll compressor



GOODLOYAL
12-09-2009, 02:17 PM
Need help :cool:,

Does anybody know maximum discharge pressure ZB76 scroll compressor?
Is it possible if dirty oil happened can reduce discharge pressure?

Thanks

nike123
13-09-2009, 03:20 PM
Maximum pressure is noted on compressor nameplate.
Still, compressor operating pressure could be relatively low but discharge superheat high.
Therefore, it is important to keep suction superheat low enough and, in that way, discharge superheat low.
Important is, that discharge gases are below 120°C.

powell
13-09-2009, 03:46 PM
What nike123 says plus here's a link to the Copeland ZB bulletin which has more information.

http://www.hvacrinfo.com/ae_index.htm

Bulletin 4-1318