Help me:confused:,
Is it ok to change mineral oil to POE from R12 compressor to use R134a?
Beside changing oil, what else i have do to compressor so my R12 compressor running well on R134a?
Shibhrac
12-09-2009, 08:34 PM
Before we start retrofitting.(converting a system from R12 into R134a) we must recover R12 in a disposal cylinder.then drain the mineral oil, add amount of polyeaster oil equal to the drained amount of oil.change all compressor's and system seals. Ask the manufacturer for ideal parts. Recharge the system with R134a and check system super heat . You may need to adjust the super heat setting or change the txv.leave the system run almost for 24 hours. Take an oil symbole and check it with reflectometer if the percentage of the mineral oil is less than 5% drain the oil once if its higher drain the oil and recheck .
powell
13-09-2009, 03:51 PM
Read bulletin 93-04 at the bottom of this Copeland AE bulletins link.
http://www.hvacrinfo.com/ae_index.htm
Classichvac
26-09-2009, 12:46 AM
Why R-134A? Do you not have a direct drop in refrigerant available. We have a drop in R414b.
No need to change oil, expansion valve etc.
Just charge with 80% of full charge. Pressure very close.:D
mkilickap
06-10-2009, 11:34 PM
thanks good a link
ko aung
12-10-2009, 04:00 PM
Thanks for this msg.
GOODLOYAL
13-10-2009, 08:43 AM
Thanks all for tips and a link. That is grat link.