View Full Version : Evaporator to air TD



kfjoe
09-09-2009, 07:51 PM
Hi all

Could anyone advise me on what a low evapotaor to air TD would indicate please ?

I have a system which in normal running has an average 10 degc TD between evaportaor sat temp and air return , but on this paticular system i am getting only 5 degc TD,
I am wondering if a compressor not running at full capacity due to broken valves etc would cause this ?

any help much appreciated

thankyou

marc5180
09-09-2009, 08:08 PM
If there is a lack of airflow across the evaporator then your Delta T will be large.

A fouled evaporator causes an abnormally small Delta T for the air.

marc5180
09-09-2009, 08:23 PM
Sorry i read your post wrong there.

Could you provide the figures you used to work out the low TD if you have them?
Including superheat and subcoolinng

nike123
10-09-2009, 10:03 AM
Are you sure in your measurements?

D.D.KORANNE
10-09-2009, 01:22 PM
An evp td has a bearing on the humidity in the cold room & it varies with product . High td means low rh & viceversa

kfjoe
10-09-2009, 01:28 PM
Thanks guys

I am basically asking if anything can change the TD of the Evap , ie inop fan , blockage , compressor not pumping to efficency etc.
or is this fixed ?


Thanks

powell
10-09-2009, 02:16 PM
Hi all

Could anyone advise me on what a low evapotaor to air TD would indicate please ?

I have a system which in normal running has an average 10 degc TD between evaportaor sat temp and air return , but on this paticular system i am getting only 5 degc TD,
I am wondering if a compressor not running at full capacity due to broken valves etc would cause this ?

any help much appreciated

thankyou

A 5 degree TD is normally too low. A high humidity box such as a flower cooler runs around a 8 TD.

Did this system work ok in the past?

You need to note all the pertinent information such as pressures, temperatures and amperage to determine the cause.

I would suspect loss of capacity due to a compressor problem, TEV problem, a restriction, low on refrigerant or maybe a dirty evap or fan motor problems.

Get all the data and work from it.

Here's a link to some troubleshooting guidelines that might help you.

http://www.hvacrinfo.com/system_trouble.htm

nike123
10-09-2009, 02:34 PM
Thanks guys

I am basically asking if anything can change the TD of the Evap , ie inop fan , blockage , compressor not pumping to efficency etc.
or is this fixed ?


Thanks

I would say that is determined by evaporator construction and materials. Since both are unchanged and air flow is probably same or lower as first day, TD could only be higher.
Are you 100% sure that your measurements and calculations is right.
Calibrate your instruments or use calibrated.