30-08-2009, 09:38 AM
Daikin split on server room tripped on HP cleared coil still tripping. Unit will start and run fine for about 5 mins then the condenser fan stops before the compressor causing pressure to rise. Is it just a faulty circuit board or am I missing something simple:confused:

nike123
30-08-2009, 09:46 AM
Faulty probe, maybe!

Kirky
30-08-2009, 09:54 AM
If its a faulty probe then why is it only stopping the fan and not the compressor please explain

nike123
30-08-2009, 10:08 AM
If its a faulty probe then why is it only stopping the fan and not the compressor please explain

If that unit has condensation control, than it could, after some time programed in controller, control condensation by switching ON-OFF condenser fan. If probe gives wrong information, than it could think that condensation is not high enough (like in cold winter days) and turn off condenser fan.
If you provide model # than we could check if that is the case here.

Kirky
30-08-2009, 01:33 PM
Got you thanks very much

jdunc2301
31-08-2009, 02:58 PM
Faulty board, we just did one, turning off condenser fan whilst running compressor then tripped HP, fitted new PCB all ok now, this was daikin technicals advice....


:D

acnerd
31-08-2009, 05:04 PM
Daikin split on server room tripped on HP cleared coil still tripping. Unit will start and run fine for about 5 mins then the condenser fan stops before the compressor causing pressure to rise. Is it just a faulty circuit board or am I missing something simple:confused:

Faulty outdoor PCB. I have done three of them already with the exact same symptoms ..... changed the PCB and all ok. :)

martinw58
31-08-2009, 09:48 PM
daikin have a fault on some out door pcbs have had same fault

Kirky
06-09-2009, 12:39 PM
Sorted it was just a faulty PCB running fine now cheers all