Dear Friends

How should be insolated the saddle of a horinzoltal tank (ammoniac separator) which will work at -35ēC.??

The tank´s volumen is 10 m3

The application is even worst because the zone where the tank will be located is a very sismic .

We want to suggest polyuretane 40 kg/m3

Thanks for yours comments
Regards
Gwapa

TXiceman
27-08-2009, 06:11 PM
You can use a saddle with a thermal break such as Oak wood or a plastic to rest the vessel on. Several ways to do this.

Or you can make the legs longer and insulate down the legs.

Ken

gwapa
27-08-2009, 06:16 PM
Thanks TXiceman
I am plannig to use hi density poliuretane 200kg/m3 for themal break but how do we tie the tank to evoid movements in a ismic situation?
Gwapa