Meer Abdulrehma
26-08-2009, 05:35 AM
Hi

Working on a trane chiller basicly have changed the condensers and placed new modules now on start up it goes through the cycle and when the unit is supposed to start the error code that comes up is Starter Transition, did not have much time to check it, any ideas what this could be will be going to the site in short while.

goshen
26-08-2009, 04:03 PM
hi if it is a star delta check your wiring on your contactors and inputs to the controler make sure u programed the the right sequence of starter type for the chiller

Meer Abdulrehma
27-08-2009, 05:39 AM
Hi

It is part winding but i will check the termination again

Meer Abdulrehma
29-08-2009, 05:28 AM
have checked the termination all is correct have checked the modules on another unit all are working ok anyadvise will be appriciated

abdulazman
29-08-2009, 12:55 PM
What is the model you're working with?
CVGE,CVHE,CVHG,CDHG. plz specify....

goshen
29-08-2009, 06:14 PM
hi there if as u said it is part winding check the contacts from the second contactor of the part winding which gives feedback to the controller i assume it is a ucp2 controler
good luck

Meer Abdulrehma
31-08-2009, 05:41 AM
Hi

Sorry did not specify earlier but The model No of the chiller is TRTAB212. Thanks Goshen will check the second contactor again thanks.

centrecipew
31-08-2009, 11:49 AM
HI, Check That contacts across J3 3+4 ( A-20 Module)close when second contactor is energised. Also check that all neutrals are conected and continuous. Check that the Hp switch has not operated on the second stage. Good luck.

abdulazman
31-08-2009, 01:55 PM
Hi meer,

Do you need the sevice setting manual (front page as an example), PM me should you require the set.

Meer Abdulrehma
31-08-2009, 03:14 PM
have tried to PM you that i need the service manual although am not sure if have done it right

goshen
31-08-2009, 04:51 PM
hi mail me at gill@gosheneng i will send u the manual
as said before check your wiring u probably missed a wire !!or a bad contact

Meer Abdulrehma
01-09-2009, 05:51 AM
Thanks Goshen have sent you mail

Meer Abdulrehma
07-09-2009, 03:53 PM
Hi Guys

Thanks to Goshen for service settings manual and abdulazman for suggesting about the manuals. this is where am at at the moment the first compressor starts with one of part winding contactors of the compressor energizing and switches off after about 5 seconds and 2nd compressor starts and runs well have set all according to manual. Could there be anything else i may have missed out am not having power from Module A20 -J7 -6

goshen
07-09-2009, 04:51 PM
check your current transformers and check for a loose or dissconnected neutral wire on the contactor , and correct wire connectiones to the module outputs

Toosh
08-09-2009, 05:27 AM
Hi, what brings in the second contactor

Norm

Meer Abdulrehma
08-09-2009, 03:24 PM
From the module A20 J7- 3 sends power to one contactor and the second get power from J7 - 6

goshen
08-09-2009, 07:28 PM
hi u could change starter cardes between the circuites and see if the problem is the card
just mark the dip switches on the cards
good luck

Meer Abdulrehma
09-09-2009, 05:33 AM
i have tried that and the card works fine on another unit i have a feeling it is related to settings but i may be wrong

goshen
09-09-2009, 04:02 PM
is the unit configured as two circuits ?
i still insist it sounds like a wiring problem

Meer Abdulrehma
11-09-2009, 05:47 AM
Hi

yes it is configured as 2 circuits

goshen
11-09-2009, 12:00 PM
then all that is left is wiring !!! or a faulty contactor
assuming all else is ok as u said u interchanged card s and it works?

centrecipew
13-09-2009, 07:37 PM
Have you checked your HP switch??
Have you got power at X2-3 and X2-12 ??
If not your HP switch is faulty.
Good luck.

Meer Abdulrehma
16-09-2009, 06:15 AM
Yes thanks for advise but am sure you do remember if the HP is disconnected nothing would run.

Have a dumb question could it be Dip Switch Settings as at moment have set Module A20-1 all Off and A20-2 123&5 on and 4 off any ideas pls advise.

goshen
22-09-2009, 07:34 PM
hi meer whats going anything new ?????

Meer Abdulrehma
23-09-2009, 03:34 PM
Hi nothing new yet but will be at the site at the end of this week will let you know thanks

goshen
25-09-2009, 11:23 AM
good luck check neutrals again hope for the best

Meer Abdulrehma
28-09-2009, 06:58 AM
Hi All

Have managed to get this unit started over the weekend the problem was no contact on the Module A20 J7-5 although the conductor was there it was not making contact so circuit was not complete. I would like to give a big thank you to all for all the support and assistance you have given to me. Thanks A Lots.